Hi,
I'm try connect to 3 DataLogger CR850 Station using GSM Callback Setting and LoggerNet , but I encountered a problem :
I only connect sussessfull first station, other station when connect ,Loggernet notice : check clock datalogger, connect unsussful, Please Help me, thank you very much !
My Setting :
Comport->Generic->Packbus Port->CR800Series
Comport->Generic_2->Packbusport_2->CR800 Series_2
Comport->Generic_3->Packbusport_3->CR800 Series_3
In Comport : Communication Enalble=true
In Generic, Generic_2, Generic_3 , tab Modem
Dial Script T "ATDphonenumber1^m" D20000
Dial Script T "ATDphonenumber2^m" D20000
Dial Script T "ATDphonenumber3^m" D20000
End Script T "+++" D1000
T "ATH^m"
and tab hardware : Baudrate 9600
In PackbusPort all 3 station :
Communication Enable=true
Pakbusport Alway Open=false
In CR800Series,CR800Series_2,CR800Series_3 :
Pakbus Address =1
Communication=true
Callback=true
I can't help on the modem side, but for one thing, all devices need to have a unique PakBus address. Using "1" for all three can be problematic.
Dana W.